reg:potential difference between phase nad neutral

Ground loops are the most common cause of AC line frequency hum in sound systems. Ground loop problems can be corrected and avoided. Also other electrical wiring related topics can be discussed here.

reg:potential difference between phase nad neutral

Postby subhu81 on Wed May 03, 2006 10:28 am

Hello Evrybody,

i am new to this group,i have a doubt which i faced during my commissioning activities in site.
these are the following things which i observed.

Incoming UPS Voltage:

Potential Difference between Phase and Neutral:230V
Potential Difference between Phase and Earth:230V
Potential Difference between Neutal and Earth:0.2v

after UPS we have a isolation transformer:after the isolation:

Potential Difference between Phase and Neutral:230V
Potential Difference between Phase and Earth:0v
Potential Difference between Neutal and Earth:0v

i cannot understand how the p.d between Phase and Earth will become 0v?pls help me.
subhu81
 
Posts: 2
Joined: Wed May 03, 2006 10:09 am

Potential difference

Postby Tomi Engdahl on Thu May 04, 2006 2:46 pm

The results you got makes perfect sense.
The reason why you got the numbers like you have in your measurements lies in the way how the isolation transformer works and how you made the measurements.

The output of isolation transformer is a floating power source. There is no connection to the ground at all through anything. When you make one connection with your multimeter between the "phase" side of isolated source, you will not get any voltage because you are essentially measuring an open circuit consisting of your grounding wire - multimeter - floating 230V output - and open circuit here. No current floating, no measurable voltage withmultimeter. Same thing happens with "neutral" side.
The isolation works. Any single one connection from either side of the isolated output will give you 0V to multimeter.


If you have two identical multimeters, and connect one from "phase" to ground and other from "neutral" to ground, you would get reading of 115V on both of them. The sum of those is that 230V. In this case your measurement circuit would consist of loop consisting of follwoign parts: floating 230V power source - multimeter 1 - ground - multimeter 2 - other end od 230V power source

If your multimeters are not ideantical, then the voltages you get on them can be different, but the sum of measured voltages would be always 230V AC within your measurement accuracy.
Tomi Engdahl
Site Admin
 
Posts: 1839
Joined: Mon Oct 20, 2003 6:15 pm
Location: Espoo, Finland

reg the potential difference between phase and neutral

Postby subhu81 on Fri May 05, 2006 8:44 am

thanks for the reply,but the transformer body ground is grounded with electrical earth whether this will make a difference for the above issue or not ?please clarify?
subhu81
 
Posts: 2
Joined: Wed May 03, 2006 10:09 am

Transforemr wirings

Postby Tomi Engdahl on Fri May 05, 2006 9:14 am

Grounding transformer body should not make any difference at least with almost all transformers in the world. The transformer body is normally built in such way that it is well electrically isolated from all transformer coils.

There could be some special transformers where some part of transformer scondary could be intentionally wired to the transformer body. I think that the pole transformers used in USA to supply power to houses (convert few kW AC to center tapped 200V AC (110V + 110V) AC) are constructed in such way that the center point of secodnary is connected to the ground/neutral connector onthe transformer, that makes also contact with the transformer body/case.
Tomi Engdahl
Site Admin
 
Posts: 1839
Joined: Mon Oct 20, 2003 6:15 pm
Location: Espoo, Finland

Re: reg:potential difference between phase nad neutral

Postby Guest on Wed Mar 02, 2011 4:20 pm

Hello everybody,

Can anyone explain me about the 0V ground systems.
Guest
 

Re: reg:potential difference between phase nad neutral

Postby Tomi Engdahl on Mon May 23, 2011 1:47 pm

Guest wrote:Hello everybody,

Can anyone explain me about the 0V ground systems.


In the typical plant or house, the 0V ground reference is most often a heavy gauge copper wire embedded around the base of the building and tied into ground rods at the corners as well as into the AC ground feeds at critical junctures.
Tomi Engdahl
Site Admin
 
Posts: 1839
Joined: Mon Oct 20, 2003 6:15 pm
Location: Espoo, Finland